I can now confirm that the on board charger, OBC, in the 2016 Kia Soul EV+ can charge at a faster rate than 12A when fed 120V. I also found that the Kia supplied level 1 EVSE charges slightly faster than the Panasonic (Nissan Leaf) EVSEUpgrade one I purchased when on the default 12A setting for 120V. Note that in the US that a circuit is not supposed to have more current draw than 80% of its rating when the current will be continuous as happens when charging an EV. This means that a 15A circuit should not have more than 12A on it which is why the EVSE that comes with the car is limited to 12A.
There has been a question about whether the OBC will draw more than 12A on 120V if given the signal that more than 12A is available. Earlier I was lead to believe that it would limit it self to 12A, which didn't make any sense to me since the OBC is a 6.6kW charger which would mean that it would have to draw 27.5A on 240V to reach that power. I suspect that 27.5A is also the limit on 120V too but I have not been able to verify that yet.
Why does this matter? If you live in a home without an available 240V dedicated circuit but you have a 120V one available you could install a high current Level 1 EVSE and shorten the charge time significantly. Also, when traveling, 20A and 30A 120V outlets are common at RV parks. If you had a portable EVSE which could be programmed up to 16A for a 20A circuit or 24A for a 30A circuit you could significantly reduce your charge time. Of course you need to understand the risks of charging at a current too high for the circuit, plug, and breaker you are connecting too. For example, I charged at 20A on a 240V 50A RV pedestal and found that the 50A breaker was warm. I would not want to charge at a higher rate than that since obviously the breaker had degraded over time from the elements. The breaker contacts were probably not clean thus increasing their resistance.
Here is the data I collected. Input voltage to the EVSE is 120VAC
The first 12A setting was the KIA EVSE. The 20A current setting was done at a different time with the car battery at a different SOC than the first ones.
There has been a question about whether the OBC will draw more than 12A on 120V if given the signal that more than 12A is available. Earlier I was lead to believe that it would limit it self to 12A, which didn't make any sense to me since the OBC is a 6.6kW charger which would mean that it would have to draw 27.5A on 240V to reach that power. I suspect that 27.5A is also the limit on 120V too but I have not been able to verify that yet.
Why does this matter? If you live in a home without an available 240V dedicated circuit but you have a 120V one available you could install a high current Level 1 EVSE and shorten the charge time significantly. Also, when traveling, 20A and 30A 120V outlets are common at RV parks. If you had a portable EVSE which could be programmed up to 16A for a 20A circuit or 24A for a 30A circuit you could significantly reduce your charge time. Of course you need to understand the risks of charging at a current too high for the circuit, plug, and breaker you are connecting too. For example, I charged at 20A on a 240V 50A RV pedestal and found that the 50A breaker was warm. I would not want to charge at a higher rate than that since obviously the breaker had degraded over time from the elements. The breaker contacts were probably not clean thus increasing their resistance.
Here is the data I collected. Input voltage to the EVSE is 120VAC
Code:
Time Current setting (A) Measured (A) % of expected time
7:40 Expected
8:10 12 11.0 106.5
8:40 12 10.4 113.0
5:55 16 14.3 77.2
21:00 Expected
11:50 20 18.4 56.3
The first 12A setting was the KIA EVSE. The 20A current setting was done at a different time with the car battery at a different SOC than the first ones.